How would you characterize the pressure drop across the length of a heatsink

Assuming the airflow across the heatsink as shown, draw a graph depicting the relationship between the pressure drop and the position along the heatsink channel.

image

The total pressure drop (ΔP) is not just frictional loss along the channels; it is the sum of three parts:

The pressure drop across a parallel plate-fin heatsink isn’t just from the friction in the channels; it’s the sum of three parts:

  1. Entry Loss: A pressure hit from the air contracting to squeeze into the narrow fin gaps.
  2. Frictional Loss: The pressure lost to viscous drag as air flows through the length of the channels.
  3. Exit Loss: Another pressure hit from the air rapidly expanding back out of the heatsink.

The main equation that puts this together is:

ΔP = (ρV²/2) * [ Kc + (f_app * L / D_h) + Ke ]

What this means for design:

  • Fin Spacing is King: This is the biggest factor. Tighter fin spacing drastically increases air velocity (V ) and reduces the hydraulic diameter (D_h ), which makes the pressure drop skyrocket (it’s proportional to velocity squared!).
  • It’s a System Thing: You can’t look at the heatsink’s pressure drop alone. It creates a “system curve.” The actual airflow you get is determined by where this curve intersects with your fan’s P-Q curve . A high-pressure-drop heatsink will choke your fan, resulting in lower airflow and worse cooling than you might expect.

In a nutshell: Pressure drop is characterized by minor losses at the inlet/exit and friction through the channels. It’s extremely sensitive to fin spacing and must be balanced with your fan’s capability to ensure adequate airflow.